    used voltage tester and part of it melted

    i used a voltage tester to see if this wire was live or not like i always do but when i touched it to yellow romex it sparked and blew a breaker i think and it melted what loooked like to be brass part of the tester. why is that is it because the wire i was testing had more voltage than it counld handle or what it kinda scrared me. it was a garden bender.



  2. #2
    pjost's Avatar
    SMF Badges of Honor

    Member since
    Apr 2014
    Location
    N & South Dakota
    Posts
    994
    Thanks
    5,151
    Thanked 2,258 Times in 682 Posts
    Between this post of yours, and this one:

    http://www.scrapmetalforum.com/scrap...ires-help.html

    I'm begging you dude, stop playing with electricity!!! You are going to kill yourself!!!
    Money is not the root of all evil, the love of money is.

  3. The Following 4 Users say Thank You for This Post by pjost:


  4. #3
    jimicrk's Avatar
    SMF Badges of Honor


    Member since
    Sep 2013
    Location
    Tennessee
    Posts
    2,826
    Thanks
    2,917
    Thanked 4,838 Times in 1,877 Posts
    After all the warnings you received on your other post and you're still at it?

    I remember when my son was messing around with an electrical outlet and got shocked. He learned a valuable lesson that day and at 2 years old was smart enough to leave the dang things alone.

    What's it going to take for you?

  5. The Following 5 Users say Thank You for This Post by jimicrk:


  6. #4
    Mechanic688's Avatar
    SMF Badges of Honor



    Member since
    Mar 2011
    Location
    Warsaw , Ind. In the heart of the lakes, and down the street from the hotel where Al Capone stayed.
    Posts
    9,568
    Thanks
    11,247
    Thanked 10,730 Times in 4,728 Posts
    Quote Originally Posted by mike1 View Post
    i used a voltage tester to see if this wire was live or not like i always do but when i touched it to yellow romex it sparked and blew a breaker i think and it melted what looked like to be brass part of the tester. why is that is it because the wire i was testing had more voltage than it counld handle or what it kinda scared me. it was a garden bender.
    Not sure what a garden bender is but it sounds like you might have had the setting on DC instead of AC, or maybe OHMs. That kind of voltage will short things out if it's not on the correct setting. It's not like testing 12 volt DC
    P & M Recycling - Specializing in E-Waste Recycling.
    If you enjoy your freedom, thank a vet.

  7. The Following 3 Users say Thank You for This Post by Mechanic688:


  8. #5
    billygoat's Avatar
    SMF Badges of Honor

    Member since
    Feb 2012
    Location
    Rochester, NY
    Posts
    630
    Thanks
    99
    Thanked 491 Times in 250 Posts
    Quote Originally Posted by Mechanic688 View Post
    Not sure what a garden bender is but it sounds like you might have had the setting on DC instead of AC, or maybe OHMs. That kind of voltage will short things out if it's not on the correct setting. It's not like testing 12 volt DC
    Exactly. I used to make a living as an electrician and I did that once myself. Wasn't paying attention and I fried the darned thing. I'm guessing you had the continuity tester on and it shorted out the circuit.

  9. The Following 2 Users say Thank You for This Post by billygoat:


  10. #6
    SMF Badges of Honor


    Member since
    Jun 2014
    Location
    Dallas/Fort Worth
    Posts
    75
    Thanks
    7
    Thanked 40 Times in 24 Posts
    Like the above said. Check to make sure it's on ac. Also I've seen meters that were for DC only and fried one. wasn't mine and a client handed it to me and sparks went flying when i tested an outlet Sounds like you just need to go buy that tester that you touch the wire to test voltage through the insulation

  11. The Following 2 Users say Thank You for This Post by Jax:


  12. #7
    SMF Badges of Honor



    Member since
    Dec 2012
    Location
    elkton,md
    Posts
    1,062
    Thanks
    8,524
    Thanked 1,470 Times in 600 Posts
    Quote Originally Posted by jimicrk View Post
    After all the warnings you received on your other post and you're still at it?

    I remember when my son was messing around with an electrical outlet and got shocked. He learned a valuable lesson that day and at 2 years old was smart enough to leave the dang things alone.

    What's it going to take for you?
    One of my older brothers taught me that lesson when I was 6, the hard way!
    Older brothers ain't they the best. Of coarse he thought it was funny.

    Op. Stop ! Listen to what people are telling you. There's a whole lot of safer way to make money scrapping.

  13. The Following 3 Users say Thank You for This Post by junkfreak:


  14. #8
    BRASSCATCHER's Avatar
    SMF Badges of Honor


    Member since
    Feb 2012
    Posts
    2,476
    Thanks
    3,436
    Thanked 3,965 Times in 1,383 Posts
    Actually I think a fork in a light socket would be a good idea for some people!!!
    I won't be wronged. I won't be insulted. I won't be laid a-hand on. I don't do these things to other people, and I require the same from them.” John Wayne-- The Shootist

    NEWBS READ THIS THREAD ABOUT REFINING!!!!
    http://www.scrapmetalforum.com/off-t...ning-read.html

  15. The Following 5 Users say Thank You for This Post by BRASSCATCHER:


  16. #9
    bigburtchino's Avatar
    SMF Badges of Honor



    Member since
    Mar 2011
    Location
    California
    Posts
    1,647
    Thanks
    4,388
    Thanked 2,835 Times in 1,132 Posts
    There's a "KNOWN" standard in ANY workplace (that wants to stay in business and keep their people healthy/living), this procedure is utilized by "TRAINED" electrical workers. This "STANDARD" is to locate and de-energize all live circuits FIRST, that workers "MIGHT" be exposed to!

    This simply means to locate a means of shutting-off or isolating the power source first. This is done before any type of "TESTING" or work is done. This done for safety and to limit the possibility of causing more equipment problems. Until you are familiar with the circuits or individual devices, you need to know how to turn the power OFF!

    So you need to locate where does the power come into the circuit, its power source (no it's not the electric company). Turn off all switches and/or breakers first. Do this before any testing or checking for "ABSENCE of VOLTAGE". The assumption has to be made by the worker that there is a possible problem and the potential for harm in all electrical work.

    You do most electrical work in a "Reverse Order", working backwards in the circuit and towards the device (wire in your case) to be evaluated. IMOP you did your "TESTING" completely "Back A$$ Wards"! I'm not trying to be mean or funny, working with electricity is serious work. This should not be done unless you are familiar with the "basic" knowledge of electrical work. This would include how, limitations and setup of the test equipment.

    Trust and believe electricity will "REACH OUT and TOUCH YOU", if you let it. You are fortunate that it was only your "Garden Bender?" that got fried, next time it might be you!

    Remember a circuit that is turned off, could still have a "Charged or Energized" condition until properly grounded.

  17. The Following 3 Users say Thank You for This Post by bigburtchino:


  18. #10
    jimicrk's Avatar
    SMF Badges of Honor


    Member since
    Sep 2013
    Location
    Tennessee
    Posts
    2,826
    Thanks
    2,917
    Thanked 4,838 Times in 1,877 Posts
    Instead of killing yourself or burning your house down why don't you take your fried volt meter and do a scrap breakdown of it. Be sure to include pictures. We like pictures.

  19. The Following 8 Users say Thank You for This Post by jimicrk:


  20. #11
    spinroch's Avatar
    SMF Badges of Honor

    Member since
    Dec 2013
    Location
    Rochester, NY
    Posts
    675
    Thanks
    1,983
    Thanked 1,556 Times in 460 Posts
    I generally wet two fingers and touch the wires. Then I measure how much my hair stands up.
    F1 Recycles

    Electronic/Electrical/Mechanical Recycling
    www.f1recycles.com


  21. The Following 8 Users say Thank You for This Post by spinroch:


  22. #12
    AdmiralAluminum's Avatar
    SMF Badges of Honor


    Member since
    Jan 2014
    Location
    Ontario
    Posts
    737
    Thanks
    824
    Thanked 968 Times in 415 Posts
    Quote Originally Posted by spinroch View Post
    I generally wet two fingers and touch the wires. Then I measure how much my hair stands up.
    I shave my head, is there a way I can use this testing method? Like what colour my skin changes afterward?
    METAL IS MY MISTRESS...PLEASE DON'T TELL MY WIFE!

  23. The Following 4 Users say Thank You for This Post by AdmiralAluminum:


  24. #13
    spinroch's Avatar
    SMF Badges of Honor

    Member since
    Dec 2013
    Location
    Rochester, NY
    Posts
    675
    Thanks
    1,983
    Thanked 1,556 Times in 460 Posts
    Yes: either measure the smoke that comes from your body, or stand in a bucket of water when you do the test and see how much boils off. Feel free to consult me for other electrical safety tips....

  25. The Following 5 Users say Thank You for This Post by spinroch:


  26. #14
    pjost's Avatar
    SMF Badges of Honor

    Member since
    Apr 2014
    Location
    N & South Dakota
    Posts
    994
    Thanks
    5,151
    Thanked 2,258 Times in 682 Posts
    When I'm bowling I think "be the ball"

    When working with electricity I think "be the fuse"

  27. The Following 5 Users say Thank You for This Post by pjost:


  28. #15
    AdmiralAluminum's Avatar
    SMF Badges of Honor


    Member since
    Jan 2014
    Location
    Ontario
    Posts
    737
    Thanks
    824
    Thanked 968 Times in 415 Posts
    Quote Originally Posted by spinroch View Post
    Yes: either measure the smoke that comes from your body, or stand in a bucket of water when you do the test and see how much boils off. Feel free to consult me for other electrical safety tips....
    Ow my belly hurts! ROTFL!

  29. The Following 2 Users say Thank You for This Post by AdmiralAluminum:


  30. #16
    spinroch's Avatar
    SMF Badges of Honor

    Member since
    Dec 2013
    Location
    Rochester, NY
    Posts
    675
    Thanks
    1,983
    Thanked 1,556 Times in 460 Posts
    Hee Hee!

  31. The Following User Says Thank You to spinroch for This Post:


  32. #17
    Metalbestos's Avatar
    SMF Badges of Honor
    Buying ewaste and vintage video games

    Member since
    Mar 2014
    Location
    Baltimore md.
    Posts
    987
    Thanks
    3,114
    Thanked 1,658 Times in 707 Posts
    Quote Originally Posted by spinroch View Post
    Yes: either measure the smoke that comes from your body, or stand in a bucket of water when you do the test and see how much boils off. Feel free to consult me for other electrical safety tips....
    Buying ewaste and video games !

  33. The Following User Says Thank You to Metalbestos for This Post:


  34. #18
    crazyguy1710's Avatar
    SMF Badges of Honor

    Member since
    Jul 2012
    Location
    Richmond,VA
    Posts
    49
    Thanks
    14
    Thanked 72 Times in 24 Posts
    This post reminds me of why we have warning labels on hair dryers and hot coffee. Oh and personally I try to lick all outlets before working on them you know just to make sure the are good

  35. The Following User Says Thank You to crazyguy1710 for This Post:


  36. #19
    smashing's Avatar
    SMF Badges of Honor

    Member since
    Jun 2014
    Posts
    142
    Thanks
    52
    Thanked 131 Times in 61 Posts
    A man shopping at Home Depot once told me the "Electrical" was French for Don't F**K With it!. Wise man

  37. #20
    SMF Badges of Honor


    Member since
    Nov 2010
    Location
    Boise, ID
    Posts
    2,702
    Thanks
    2,237
    Thanked 2,352 Times in 1,014 Posts
    Gardener Bender is what he meant. They make electrical tools.

    If you want to continue playing with electricity, how about getting a non contact tester? You can even amuse small kids by rubbing it across your clothes really fast and triggering the tester.

  38. The Following User Says Thank You to IdahoScrapper for This Post:



  39. Similar threads on the Scrap Metal Forum

    1. Connecticut | For Sale - dimm ram tester
      By chrisc in forum Scrappers Classifieds
      Replies: 8
      Last Post: 08-30-2013, 03:24 PM
    2. Recommendation for a RAM tester?
      By Mick in forum Tools and Equipment
      Replies: 5
      Last Post: 08-24-2013, 06:27 PM
    3. Hard Drive Tester
      By HammerTime in forum General Electronics Recycling
      Replies: 21
      Last Post: 12-01-2012, 06:30 PM
    4. Laptop battery tester?
      By MvPElectronicRecycling in forum General Electronics Recycling
      Replies: 6
      Last Post: 09-09-2012, 03:01 PM

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

 
Browse the Most Recent Threads
On SMF In THIS CATEGORY.





OR

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

The Scrap Metal Forum

    The Scrap Metal Forum is the #1 scrap metal recycling community in the world. Here we talk about the scrap metal business, making money, where we connect with other scrappers, scrap yards and more.

SMF on Facebook and Twitter

Twitter Facebook