    air conditoner guy advice preferably from a hvac or someone with knowledge of this.

    this air conditioner guy told me this when i asked him you know the landlord said i could have this right and he said he had to take it because of the epa and he said if i let it out here i would get a 50,000 dollar fine and i have to take this its epa regulations and taking the unit is kinda my bit is what he said. i thought the person who owned the ac unit could keep it and just have the oil and gas drained by a tech guy in the phone book for a fee is this not true? i asked our landlord if i could have the ac and he said yes but then i told the guy that was doing the ac that he told you i could have it right and then he gave me the speal is it true what he said? i asked him if he could drain it there and he said he would have to bring his reclaiming stuff back and do it but i think he just wanted to scrap it out himself. the landlord also got some other guy before the one that did the ac he said when i asked him about the radiator if i could have it and he said yes he didn't care thats why i was shocked when the guy that did the ac denied me the ac unit. he said he talked to the landlord this morning and the landlord told me nothing about it and just left for work so i found this out from the ac guy which also did not make me very happy. they can reclaim the gas and oil at your house right? they dont have to take it with them do they?



  2. #2
    SMF Badges of Honor


    Member since
    Nov 2011
    Location
    boise, ID
    Posts
    1,605
    Thanks
    469
    Thanked 1,462 Times in 668 Posts
    Mike, the proper term is recover not reclaim. A lot of techs just evacuate the units and take them to whomever recycles them. As far as the oil, only the person recycling the compressor is responsible for the oil. But in a lot of states you either have to have a HVAC license or be a licensed recycler to sell the coils to a scrap yard.

  3. #3
    mthomasdev's Avatar
    SMF Badges of Honor


    Member since
    Apr 2012
    Location
    pittsfield, ma
    Posts
    1,300
    Thanks
    348
    Thanked 1,532 Times in 704 Posts
    Adding to what Joe said - EPA can assess a fine of $37,500 for the intentional release of refrigerant. There is also a potential reward for reporters of this activity. A lot of contractors take the salvage value into account when bidding thier work. The refrigerant alone in that unit could be worth a significant amount of money, not to mention the coils, compressor, motor and copper. Most contractors would be willing to allow the owner to keep the unit, provided they either didn't want it or they knew about ahead of time. Personally, I wouldn't expect a contractor to believe a tenant about something like that. Yes, you can get them drained by professionals, but what is that going to cost you. My guess to have an hvac guy come to your house and do it is at least a 1 hour charge at 75 per hour. What is left after you pay that?

  4. #4
    eesakiwi's Avatar
    SMF Badges of Honor



    Member since
    Dec 2010
    Location
    NZ
    Posts
    2,531
    Thanks
    2,909
    Thanked 2,556 Times in 1,227 Posts
    There's probably something in the Tradesman's job contract like to 'Remove old unit and replace with....'

    Its sorta says there that he has to remove it. First he has to remove it from its footing, and then the property.
    The guys got his whole business to look after. Its a part of 'Due process'.

    If after taking it it (its in his hands at the time) he did give it to you, and you scrapped it and went to sell it, the first thing they will ask about if "What happened to the Freon?".

    And if your answer is "Oh I just let of out " You are in big trouble. If you then mention anything about the Tradesman, so is he.

    Like for him to give it to you, he knows you are not going to recover the gas at all. In knowing that, he's part of it too.

    I wouldn't believe anything a random person said to me if I was that Tradesman either. It defiantly would not be the first time somebody's said that to him.
    Last edited by eesakiwi; 06-04-2016 at 04:14 AM.

  5. The Following User Says Thank You to eesakiwi for This Post:


  6. #5
    wayne1956's Avatar
    SMF Badges of Honor



    Member since
    Aug 2010
    Location
    Cleburne, TX
    Posts
    705
    Thanks
    195
    Thanked 754 Times in 293 Posts
    Actually, in this case the answer would be, the HVAC person who replaced the unit drained the Freon. For the HVAC person to replace the unit, he has to drain the old unit of Freon, and once that is done the old unit no longer has the Freon in it, and it can then be processed. I have about half a dozen central units I am waiting to process (time constraints) that I have received from an apartment complex that I haul off all their appliances and AC units. All were replaced by their certified HVAC maintenance person, and as such had the Freon drained before the new unit installed.

    Quote Originally Posted by eesakiwi View Post
    There's probably something in the Tradesman's job contract like to 'Remove old unit and replace with....'

    Its sorta says there that he has to remove it. First he has to remove it from its footing, and then the property.
    The guys got his whole business to look after. Its a part of 'Due process'.

    If after taking it it (its in his hands at the time) he did give it to you, and you scrapped it and went to sell it, the first thing they will ask about if "What happened to the Freon?".

    And if your answer is "Oh I just let of out " You are in big trouble. If you then mention anything about the Tradesman, so is he.

    Like for him to give it to you, he knows you are not going to recover the gas at all. In knowing that, he's part of it too.

    I wouldn't believe anything a random person said to me if I was that Tradesman either. It defiantly would not be the first time somebody's said that to him.

  7. #6
    F350scrapper's Avatar
    SMF Badges of Honor


    Member since
    May 2014
    Location
    Minnesota
    Posts
    156
    Thanks
    71
    Thanked 151 Times in 68 Posts
    In order for a unit to be taken off the house the freon is recovered as you have to cut the copper piping running into the house before replacing it. So if it was just laying there it was already recovered.

  8. #7
    greytruck's Avatar
    SMF Badges of Honor



    Member since
    Jan 2012
    Location
    Thornton, Illinois
    Posts
    1,873
    Thanks
    1,639
    Thanked 1,733 Times in 893 Posts
    Quote Originally Posted by F350scrapper View Post
    In order for a unit to be taken off the house the freon is recovered as you have to cut the copper piping running into the house before replacing it. So if it was just laying there it was already recovered.
    Not always true. I use to believe this also. Central air units can be removed from the house and still be charged.

  9. The Following 2 Users say Thank You for This Post by greytruck:


  10. #8
    mike1 started this thread.
    mike1's Avatar
    SMF Badges of Honor


    Member since
    Dec 2011
    Location
    Rochester indiana
    Posts
    553
    Thanks
    231
    Thanked 93 Times in 76 Posts
    Quote Originally Posted by wayne1956 View Post
    Actually, in this case the answer would be, the HVAC person who replaced the unit drained the Freon. For the HVAC person to replace the unit, he has to drain the old unit of Freon, and once that is done the old unit no longer has the Freon in it, and it can then be processed. I have about half a dozen central units I am waiting to process (time constraints) that I have received from an apartment complex that I haul off all their appliances and AC units. All were replaced by their certified HVAC maintenance person, and as such had the Freon drained before the new unit installed.
    so the fact that he didnt have the tools with him to reclaim the gas but he also told me before that. that the freon was gone from it that it leaked out is this a lie and he just wanted to recycle it himself? he told me he had to take it to reclaim it.

  11. #9
    mthomasdev's Avatar
    SMF Badges of Honor


    Member since
    Apr 2012
    Location
    pittsfield, ma
    Posts
    1,300
    Thanks
    348
    Thanked 1,532 Times in 704 Posts
    Quote Originally Posted by F350scrapper View Post
    In order for a unit to be taken off the house the freon is recovered as you have to cut the copper piping running into the house before replacing it. So if it was just laying there it was already recovered.
    This belief will get you in trouble one day. Most central air units have valves that can be closed to isolate either the condenser and or the evaporator. If one of these units is being replaced, the valves can be closed and the refrigerant in the lines between them removed. New units (with refrigerant already in them) are reconnected and additional refrigerant is added to fill the lines in between. I have a unit sitting in my driveway right now. Guy I got it from thought it was drained. Label says it has 7 pounds of R22. I know that I'm not taking a chance. I'll hook up the Apion and pull the required vacuum and see what I get. Either way, it's better than taking a chance and getting fined, not to mention the environmental concerns.

  12. The Following 3 Users say Thank You for This Post by mthomasdev:


  13. #10
    eesakiwi's Avatar
    SMF Badges of Honor



    Member since
    Dec 2010
    Location
    NZ
    Posts
    2,531
    Thanks
    2,909
    Thanked 2,556 Times in 1,227 Posts
    I expect that after the units had its Freon reclaimed, the operator has to 'Tag' it with identification etc etc.

    Also I have found several Heatpump units with the Freon still in it. There's a tap they close off and then they undo the connections to the joining pipes, and remove the outside, or inside, or joining, unit.

    Also, I have tipped over fridge compressors that have sat there for days, open to the air, and suddenly had the oil squirt out under pressure, everywhere, very messy, expeshly when it happens inside.
    There's one way valves inside it, they will hold pressure for quite a while.

  14. The Following 2 Users say Thank You for This Post by eesakiwi:


  15. #11
    wayne1956's Avatar
    SMF Badges of Honor



    Member since
    Aug 2010
    Location
    Cleburne, TX
    Posts
    705
    Thanks
    195
    Thanked 754 Times in 293 Posts
    Wow, never knew about the valves. Learn something new every day. Thanks for the info.

  16. #12
    SMF Badges of Honor


    Member since
    Nov 2011
    Location
    boise, ID
    Posts
    1,605
    Thanks
    469
    Thanked 1,462 Times in 668 Posts
    Eesakiwi, the oil is spraying out of the compressors because the units were not properly evacuated. Refrigerant is trapped under the oil in the compressor. If you don't hit the compressor with a hammer when you are evacuating the unit, you will not get the refrigerant that is trapped under the oil.

  17. The Following 5 Users say Thank You for This Post by freonjoe:


  18. #13
    SMF Badges of Honor



    Member since
    Apr 2015
    Posts
    2,076
    Thanks
    616
    Thanked 2,446 Times in 1,093 Posts
    When the unit is running some oil travels along with the freon, the oil become saturated with oil in the same way your soda pop has carbon dioxide to give it the fizz. Let an open bottle or glass of pop sit for a day or so it becomes flat.

    To completely evacuate a unit it should be drawn down into a vacuum, to turn the remaining freon into vapour by boiling yes that is correct boiling. By introducing a vacuum into the system we are lowering the boiling temperature of freon turning it into a vapour which the recovery unit turns back into a liquid as the freon is being pumped into a receiver used to ship the recovered freon to a recycler.

    Sometimes a refrigeration or AC unit becomes wet with water contamination, on commercial units which are equipped with a sight glass the green dot in the middle will change colour if there is water present. Water freezes causing an ice ball to form where the freon is exiting from the capillary tube or sporlan valve intio the evaporator. The ice ball prevents the flow of freon which caurses the unit to build up an excess of pressure possibly damaging the compressor if your lucky just stop cooling of go into a loop where the over load continually tries to start the compressor which will not start as long as the ice ball is blocking the system from passing freon as a gas.

    Ok, now to remove this water we have to first evacuate the system of freon once this is accomplished we now put a vacuum pump to the shrader valve we initially installed to evacuate the system. This vacuum pump is made especially for this job and will pull a vacuum into the microns, now were going to get more freon then any water in the system is going to also boil off as a vapour.

    Good time to replace the compressor oil as the water mixed with the oil and freon created acids that are harmful to the motors insulation, that done we install a new filter drier then replace the freon with new.

    If we were to pump liquid freon out of the unit we would stand a chance of hydraulicing the piston causing the recovery pump to lock up, break a connecting rod or damage the reed valves.

    Evacuating a unit is time consuming so most guys will tap into the high side removing liquid freon, to do this the compressor on the unit being evacuated must run in order to make liquid, once there is no more liquid freon coming out the technician signs off the job and goes home leaving saturated oil inside the compressor but saved 3/4 of an hour and gets paid the same money had he put in the time to do a proper job.

    You wont find many refrigeration technicians claiming to enjoy this part of the job and this is perhaps a good reason for many a scrapper to approach a licensed tech to work as an apprentice. If you were competent at your work I do not believe the technician would have to be present to oversee your work he might have to sign off though so marshalling all your units into one easy location would make that part of his requirement easy.


    AC units usually use multiple capillary tubes, liquid freon from the high side makes it way through the tubes which unite at the evaporator, the liquid freon as it leaves the cap tubes become a gas that absorbs heat. To us humans the air passing over the evaporator coil is cool and refreshing.

    Large commercial units use a sporlan valve which are pretty cool valves that have a needle valve inside the technician is able to make adjustments that control the flow of liquid being turned into a gas. The more freon available to turn into gas make it a cooler or walk in freezer.

    On the bottom of the sporlan valve below you see a cap screw, you remove the cap screw to make the adjustments. The copper line attached to the top of the valve is what controls a bellow that works the needle valve. By turning the adjustment screw in your adding more pressure to the spring which in turn cuts down on the flow of freon if you want the box to be colder back the screw out thus allowing more freon to pass through the system.



    Last edited by alloy2; 06-08-2016 at 12:45 AM.

  19. #14
    eesakiwi's Avatar
    SMF Badges of Honor



    Member since
    Dec 2010
    Location
    NZ
    Posts
    2,531
    Thanks
    2,909
    Thanked 2,556 Times in 1,227 Posts
    This, quote{Large commercial units use a sporlan valve which are pretty cool valves that have a needle valve inside the technician is able to make adjustments that control the flow of liquid being turned into a gas. The more freon available to turn into gas make it a cooler or walk in freezer.

    On the bottom of the sporlan valve below you see a cap screw, you remove the cap screw to make the adjustments. The copper line attached to the top of the valve is what controls a bellow that works the needle valve. By turning the adjustment screw in your adding more pressure to the spring which in turn cuts down on the flow of freon if you want the box to be colder back the screw out thus allowing more freon to pass through the system.}
    ~~~~~~~~~~~~`

    This is exactly what I have been wanting to know for a while, but didn't know the question to ask......
    I was wanting to make a cooler unit to use with a receiving flask on a laboratory distillation setup. The water chillers only get down to just under freezing, and a home freezer gets down to -14°C when running 100% of the time. They are too bulky to use.

    I will check my water chiller to see if its got that valve on it tonight.
    If it hasn't maybe I can get it changed, and maybe a different gas if that helps. Theres a small fridgeration firm near here that I can use to do it.

    And... thanks again Alloy2.

  20. The Following 2 Users say Thank You for This Post by eesakiwi:


  21. #15
    SMF Badges of Honor



    Member since
    Apr 2015
    Posts
    2,076
    Thanks
    616
    Thanked 2,446 Times in 1,093 Posts
    Quote Originally Posted by eesakiwi View Post
    This, quote{Large commercial units use a sporlan valve which are pretty cool valves that have a needle valve inside the technician is able to make adjustments that control the flow of liquid being turned into a gas. The more freon available to turn into gas make it a cooler or walk in freezer.

    On the bottom of the sporlan valve below you see a cap screw, you remove the cap screw to make the adjustments. The copper line attached to the top of the valve is what controls a bellow that works the needle valve. By turning the adjustment screw in your adding more pressure to the spring which in turn cuts down on the flow of freon if you want the box to be colder back the screw out thus allowing more freon to pass through the system.}
    ~~~~~~~~~~~~`

    This is exactly what I have been wanting to know for a while, but didn't know the question to ask......
    I was wanting to make a cooler unit to use with a receiving flask on a laboratory distillation setup. The water chillers only get down to just under freezing, and a home freezer gets down to -14°C when running 100% of the time. They are too bulky to use.

    I will check my water chiller to see if its got that valve on it tonight.
    If it hasn't maybe I can get it changed, and maybe a different gas if that helps. Theres a small fridgeration firm near here that I can use to do it.

    And... thanks again Alloy2.
    Chances are any appliance in your home using freon will use capillary tubes instead of the more expensive sporlan valve aka expansion valve.


    A handy capillary tube chart, I believe sporlan is trade name for the expansion valve. http://www.jbind.com/pdf/inst-tubing.pdf

    Here's youtube video with a reasonable explanation on the use of capillary tubes.

    Last edited by alloy2; 06-08-2016 at 10:23 AM.

  22. The Following User Says Thank You to alloy2 for This Post:


  23. #16
    SMF Badges of Honor



    Member since
    Apr 2015
    Posts
    2,076
    Thanks
    616
    Thanked 2,446 Times in 1,093 Posts
    Alloy2 is putting out an SOS to you guys that dismantle washing machines I need the paper tucked away inside the console that has the wiring schematics along with timer sequence.

    A digital copy will suffice.

  24. #17
    SMF Badges of Honor


    Member since
    Nov 2011
    Location
    boise, ID
    Posts
    1,605
    Thanks
    469
    Thanked 1,462 Times in 668 Posts
    Gus, do you have a model number?

  25. #18
    SMF Badges of Honor



    Member since
    Apr 2015
    Posts
    2,076
    Thanks
    616
    Thanked 2,446 Times in 1,093 Posts
    Quote Originally Posted by freonjoe View Post
    Gus, do you have a model number?
    No, I was hoping the part number from the schematic would lead me to the model of timer used.

    The reason I want this data from various machines is that I'm going to build a pen plotter that will attach to the wiring harness of the timer then when it's powered up the plotter will chart each sequence to see if they're operational.

    I'm still figuring out in my mind how I want this test unit to react with the internal contact points within the timer, thinking that I may add a resister to add a load to each contact as it engages this way I'll be sure after bench testing a timer it will work in a washing machine. This way I can stand behind my product guarantee with confidence.

    There must be a master chart listing timer sequences, then with my pen plotter would be able to identify an unknown timer by simply recording the sequences then matching the output data with the master chart.

    As your probably already aware the majority of timers use a common contact block containing a full house of contacts, it depends on the features of the washing machine as to how many of those contacts will be used, the cam built into the timer operated by the clock motor depicts which contacts will be used.

    The following would be required on every machine, timer power on, cam advances once the water level switch contacts close, timer motor advances the cam forward to close contacts to start main motor to run agitator, timer advances slowly during the wash cycle to a soak period, timer motor cam is programmed for the soak time require, perhaps at this time another set of contacts engage to activate the drain pump to add fresh water during a spin cycle in spurts, the contacts inside the timer at this point would not call on the water level switch but that if the solenoids from the fill valves user would have chosen hot or cold rinse.

    Anyhow it's the sequence data that I'm after so that I can compile my own master list.

    I do not want to get back into repairing appliances I hate dealing with the public, I'm retired and would like something simple to do with my time.

    By the way Danfoss has some excellent apps for your smart phone, be sure to check these out you might find one that is useful. I installed a few this morning.
    Last edited by alloy2; 06-08-2016 at 01:30 PM.

  26. #19
    SMF Badges of Honor


    Member since
    Nov 2011
    Location
    boise, ID
    Posts
    1,605
    Thanks
    469
    Thanked 1,462 Times in 668 Posts
    So you just want ester charts?

  27. #20
    SMF Badges of Honor



    Member since
    Apr 2015
    Posts
    2,076
    Thanks
    616
    Thanked 2,446 Times in 1,093 Posts
    Quote Originally Posted by freonjoe View Post
    So you just want ester charts?


  28. Similar threads on the Scrap Metal Forum

    1. How Good Is Your Knowledge of these
      By 1956 in forum Scrap Metal Questions and Answers
      Replies: 29
      Last Post: 03-17-2014, 06:12 PM
    2. Need more knowledge
      By painnbt in forum Introduce yourself
      Replies: 3
      Last Post: 10-13-2013, 11:00 PM
    3. Score, motherload, or otherwise awesome thread. - SMF Knowledge is $$$
      By foobar in forum A Day in the Life of a Scrapper
      Replies: 3
      Last Post: 08-12-2013, 09:00 PM
    4. Appreciate the knowledge at SMF!
      By bluehorse in forum Introduce yourself
      Replies: 7
      Last Post: 04-24-2013, 02:38 PM
    5. I need some knowledge, please help.
      By scrapaddict in forum Scrap Metal Tips and Advice
      Replies: 26
      Last Post: 05-25-2012, 11:56 PM

Page 1 of 2 12 LastLast

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

 
Browse the Most Recent Threads
On SMF In THIS CATEGORY.





OR

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

The Scrap Metal Forum

    The Scrap Metal Forum is the #1 scrap metal recycling community in the world. Here we talk about the scrap metal business, making money, where we connect with other scrappers, scrap yards and more.

SMF on Facebook and Twitter

Twitter Facebook